Powerflex 750 series VSD - fault reset parameter
nylie2
Mar 2012
Brisbane
I need some help on how to reset fault on the Powerflex 750 via ladder logic.
I have looked through the parameter documentation and I could not find any parameter related to clear fault on VSD. The only other parameter I found was P156 which is a digital input.
Does anyone know of any other parameter that I can use to do a software reset for the fault on the VSD so I can assign it to datalink and use it in ladder logic?
Thanks.
How are you communicating with the drive? Are you using the ladder logic in the drive? is it a powerflex 753 or 755. We need some more informatio to help ypu out.
The drive that I am using is both powerflex 753 and 755. Communication is via Ethernet/IP and the ladder logic is from a controllogic rack which is separate from the drive.
Basically what I intend to do is to set the fault reset parameter to a datalink output data in the module defination page. From there I will use the datalink tags in rslogix ladder logic.
Easier than it looks: Bit 03, "Reset"
You don't need messaging or parameters or DataLinks.
I presume you're connecting to the drive over a network and have the Command Word defined or mapped somewhere in your controller.
Bit 03 of the Command Word is always* the Reset command for an Allen-Bradley variable-speed drive.
When you set that bit true, the drive should reset any resettable faults.
The Command Word is described in detail in Appendix D (page 235) of the PowerFlex 755 embedded EtherNet/IP adapter user manual.
* For all the drives I'm familiar with and can think of right now, using most network adapters.
If you add the drives into your project, the tags are created for you. I have attached a version 19 example for you to look at.
Hi Ken & Kev,
I found the tags now. Didn't realize they were located in such an obvious location.
Thanks for the help.
Looking over the technical data for a PowerFlex 755 & noticed they specify a minimum enclosure volume for their drives: (1)When using a circuit...
548
I keep getting a Net IO error message F037 on a brand new drive and after researching it, AB says that it has to be connected to a managed...
2,279
Hi everyone, I have this issue with a PowerFlex 755 that it mount a Safe Speed Monitor option module. Frequently, while running, appear the error...
2,335
Hi, I am just starting with the drives and I have a Powerflex 750 drive which is missing the rating plug board from the inverter board. I check...
665
Is anyone else having looooong connecting times when using CCW to a 750 via a 1203-USB? It is taking upto 10 minutes to connect to drive or...
1,786