I need to develop logic for controlling the flow through 8 media filters with a Siemens S7. The flow will be divided by the total number of filters that are online. That is the easy part. A PID will monitor the effluent flow from each individual filter and modulate the effluent valve.
Where I am running into trouble is with the development of a "flow trim" based on filter performance. This Trip will be 10-20% of the control loop.
The idea is for filters with higher turbidity to receive less flow and the filters with the lowest will see more flow.
So for example:
(Max allowable flow through any given filter = 1MGD)
Filter 1 Turbidity 0.08 -> Eff Flow 1.00 MGD
Fitler 7 Turbidity 0.10 -> Eff Flow 0.95 MGD
Filter 5 Turbidity 0.15 -> Eff Flow 0.90 MGD
Filter 2 Turbidity 0.20 -> Eff Flow 0.85 MGD
Fitler 4 Turbidity 0.20 -> Eff Flow 0.80 MGD
Filter 3 Turbidity 0.25 -> Eff Flow 0.75 MGD
Fitler 6 Turbidity 0.27 -> Eff Flow 0.65 MGD
Filter 8 Turbidity 0.30 -> Eff Flow 0.60 MGD
Let me know if you have any ideas or need me to clarify. Thanks!
I have 14 assembly lines and an LED display with a siren looking light and a list of 18 tunes. There are 3 cells (each cell is 4-5 assembly...
2,099
Kindly, we have the following configuration fault on a Kinetix 5700 axis. It only appears when we go online on the Plc. We are just starting the...
100
When supplying variable frequency drives (vfd), should we install the line filter (emc) before the reactor (choke), or reactor before filter...
199
Hi. I'd like to have a filter on an Alarm Summary page where I could pick which of the 3 groups I created I want to display on the screen. I...
556
Good morning, I'm new to PLC and HMIs, and I was given the following problem: I need to be able to filter alarms and events that are only related...
392