Problem in an Input card 1746-IA16
AB2005
Nov 2006
Lahore
319
I have an SLC 5/03 with I/Os in one of our machine. I am facing a problem with an Allen Bradley PLC Input card 1746-IA16 (85-132VAC) that voltage at its terminal block of an input (not specific, some time 5, some time 8 or some time 12 etc.) is high but related LED doesn’t ON and no operation performs by PLC for related input. I have replaced 3 cards till now due to this problem but could not understand that why it happens. The supply voltage remains between 110-120VAC.
I need assistance to overcome on this problem.
The two bottom terminals of a 1746 IA16 is a common terminal that has to have a wire connected to it .
Is that wire connected to a neutral terminal .
Test your high input terminals to the common to confirm its good.
I found some problem in grounding of control power transformer 380/110V which was an Auto Transformer. I installed an Isolated transformer and connected one output point (110V) with ground.
why you did not try to get a direct line from the transformer (120v a.c.) to that input to confirm is it a plc problem or power problem !, this should be step one in troubleshooting before replacing 3 input modules!
Hello Guys, I have a problem regarding with my PLC communication, I have a module card 1734-IB4, everytime I triggered the input ch 0, the light...
1,568
Hello, I have just installed an 1734-IE2V Point IO Analog Input Card and calibrated it. I used ground for the low reference and a DC source set...
3,780
Hi Experts, I would like to share one prb with you experts, on one of my site i have Control Logix Redundant System with 2 I/Os Chassis. I have...
3,421
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
18
1,425
I have 1769-IF4 module and 1766 micrologix 1400 series B controller, when connecting Analogue input in module it's showing maximum values of...
1,696