Redundant Module Error 1757-SRM
Hanjaya
Jun 2009
Jambi
dear all,
I have problem with RSlogix5000 Redundancy Module, Redundancy Module of Primary Controller is Showing Message FRMW ERR and the Status of secondary Controller is not RUN (Light Off) with status of its Redundancy Module Disqualified.
I Attached my RSLinx Status Display
Please Respond...
Regards
Hanjaya
:confused:o_O:confused:o_O:confused:o_O o_Oo_Oo_O 🔨
Your 1757-SRM Redundancy Module has definitely failed. The "FRMW ERR" message indicates a Firmware Error. If a power cycle does not cause the module to recover, you may need to replace the module.
You should get in touch with Rockwell Automation Technical Support in Indonesia, 001 8036 1008.
They will need to know which Firmware Revisions you are running in all of your modules, and will need to know more information about the configuration of the system, and about any recent changes you might have made to the program that preceded this error.
Thanks for Reply Ken,
I have already turn off the secondary controller and disconnect the error redundancy module, when i install the module back its show "????"
and i turn on the secondary controller, but the controller still not run with redundancy module still disqualified.
I also try to swap the redundancy module, but the result still the same.
I have a problem with AI module (1756 IF16) error (module fault: 16x0009, additional fault code:16x0001). Explanation for the error is: 0x0009...
4,639
Hello I would like some guidance on the correct way to install a new input module on a redundant Control logix system using control net on a...
1,040
Hello. What is the right procedure for online change of AI module configuration parameters (input range) with redundant AI modules (over...
2,491
Hi, Does anyone know if we can put a Prosoft Modbus module in the ControlLogix redundant CPU Chassis each? Will it cause any negative effect to...
3,361
Hi All, Has any of you tried to change the IP Gateway of the PLC (of course, essentially of the ENBT card), while in a redundant configuration...
128