Remote Control of valve on/off

bornwild

Member
Join Date
May 2010
Location
Riyadh
Posts
429
Dear all,

We would like to remotely turn off/on flow to many units for chilled water flow for a pipe size varying from DN 15 To Dn 32. Are there any cheap brass valves which will allow us to do so via gprs or lan. What would be the best solution for the same. We have around more than 1000 units where we would like to implement this. As of now ,we do it manually by closing the ball or gate valve. Waiting to here from the experts here.

Note:this is a commercial tower of 45 floors.
 
Dear all,

We would like to remotely turn off/on flow to many units for chilled water flow for a pipe size varying from DN 15 To Dn 32. Are there any cheap brass valves which will allow us to do so via gprs or lan. What would be the best solution for the same. We have around more than 1000 units where we would like to implement this. As of now ,we do it manually by closing the ball or gate valve. Waiting to here from the experts here.

Note:this is a commercial tower of 45 floors.

GPRS or LAN is a transmission system, not a protocol, what protocol and software system are you going to use to message them to open/close ?

Can you not just use a solenoid valve and design your system accordingly with remote I/O to be operated from a PLC or whatever PLC/BMS system you have on site ? What i mean is something like this:

https://www.bellflowsystems.co.uk/b...9jB6lOQFCKuFCUU8ewQb8WVnJfAMpkAm2tBoC5cnw_wcB
 
Last edited:
+1 for Johnson.

We have used el-torque for something similar (10 valves, not 1000) not long ago (maritime application)

CAN-bus or LON-bus should fit your bill too.
 

Similar Topics

Hello Dear users, I am writing about a problem that has been bothering me for a few days, i.e. I am trying to establish remote access to the Allen...
Replies
0
Views
95
I have to provide remote access and control to a touch screen. I was thinking about using Weintek and the Weincloud. Does anyone know if this is...
Replies
11
Views
615
Hello everybody, I am working for an OEM and we are in the process for trying to raise the effectiveness of the pretesting of machines. Basically...
Replies
20
Views
672
Whenever I try and change display pages on my Panelview Plus 7 from the remote display change the screen errors out like it has a communication...
Replies
6
Views
1,506
Hey guys, Wanted to make a thread so you guys can teach me things! 🔨 Anyways, I have a powerflex 525 that has a control module outside of...
Replies
5
Views
947
Back
Top Bottom