Set max torque permissive value in PowerFlex 525

Bering C Sparky

Lifetime Supporting Member
Join Date
Mar 2014
Location
Bering Sea, Alaska
Posts
1,117
Hello,
Would anyone happen to know what parameter in a PowerFlex 525 to have the drive trip if the torque permissive set point is exceeded?

I have a conveyor that is breaking flights off a small box elevator when the box gets stuck on the flights. Need to limit the torque allowed so the drive will trip if a box gets stuck.

I just looked though the manual and nothing jumped out at me.

If anyone who is familiar with the PF 525 knows the parameter off hand I would appreciate it. I will keep looking as well.

Thanks
 
Are you looking for the shear pin settings?

Shear Pin1 Level A486
Shear Pin 1 Time A487
Shear Pin2 Level A488
Shear Pin 2 Time A489
 
Are you looking for the shear pin settings?

Shear Pin1 Level A486
Shear Pin 1 Time A487
Shear Pin2 Level A488
Shear Pin 2 Time A489

Not sure, I have not heard that term used for drive parameters before.
Been working with AD Dura Pulse GS3 drives the past 8 years and they had a parameter to set max allowable torque and you could open the relay output when that value was exceeded.

This is my first dealing with the a Powerflex drive in 8 years so I have some reading to get back in the swing of the parameter set up and terminology.
They used multiple brand drives on this new build ship so lots to take in this season.

I will check out the parameters you show above and see if that will work.
I just need the drive to trip if the torque on the motor exceeds set point value.

Thanks
 

Similar Topics

Hello, I have an unused IC200CPUE05 Versamax PLC which I assume to be completely default settings. I'm trying to set an IP and download...
Replies
6
Views
2,162
Hi everybody, I am trying to set PCL time and date from iFix VBA code and I don't even know where to start. Does anybody know the command or...
Replies
3
Views
2,649
Hey All, Im new to this (hence the name) can someone direct me in the right direction? I am using a slc500 (fixed 20 I/o) with pic 1747...
Replies
7
Views
1,747
Dear Sirs / Experts We have encountered a "Nmax TRIP" on our EVS9327-ES LENZE servo drive. I have tried resetting from PC by changing the...
Replies
0
Views
3,135
Hello, Wondering if anyone here remembers how to set the maximum number of S7 & MPI connections allowed for a PLC. I feel like it should be in...
Replies
4
Views
4,268
Back
Top Bottom