Hmmm, it didn't work when I connected a Fluke signal processor (Fluke 754).
I set up the Fluke to output 4mA and connected the leads to 0+ and 0- terminals (for channel 0). At 4mA, I got 32767 and it stayed at that value.
Anyone know what I'm doing wrong?
Thanks
Cancel this question:
I was in RUN mode - I had to do a STOP, then do "Download to Device" then select "Hardware and Software (only changes)". After that it worked fine.
Nice linear relationship now.