Siemens S7/TIA v16: Why isn't HMI recognising PLC tags?...
Mas01
Oct 2020
Leicester, England
1,109
I'm a bit lost.
I don't understand why my HMI (Simatic 1200) is not recognising any PLC tags.
From the ethernet comms page , all seems OK.
Yet when I try to make the link between the HMI tag and its PLC counterpart, "PLC" appears in pink, as though it is unrecognised.
Anyone know what I'm doing wrong?
PLC-HMI LINK.jpg 2 Values to be displayed.png 3 Why are these not recognised.png
Looks like the tag table isn't set up right. On your second post, if you click the box with the three dots next to the tag box, you can assign a PLC tag to the HMI directly. This will add the tag to your HMI tag table and sort out the connections.
You can also add tags in bulk by just highlighting everything you want from the PLC tag table and copy/paste to the HMI tag table.
Your 'PLC' connection is in pink because it doesn't recognise it. Your actual plc name in your project is 'PLC_1'.
In the project tree go to the connections just below the HMI tags and set the connection correctly.
You will probably then need to set that connection to your tags where the pink bit is.
Thanks for this.
This is what is on the Connections...
Go to connections, delete PLC, then add new and enter the correct addresses for your setup. In your current PLC connection there is nothing in the partner or node columns so it doesnt know what its trying to connect to.
Actually, just a thought. Highlight the PLC connection, then in the parameter section below see if you have the correct ip adresses and interface set as ethernet and access point as S7online
Try adding a new hmi and it should pop up and ask you if you want to create a connection to a plc in the priject and create that automatically. You can the copy and paste your screens over and delete the original one
I did that, thanks,...it's looking a bit healthier because the station/node/partner fields are filled in...
@puddle, @bb76
MANY THANKS! It's working finally!
The two PLC tags I want displaying are being displayed on the HMI screen at last!
As well as your suggestions, there was a firmware "missing panel image" problem (thread here: https://www.plctalk.net/qanda/showthread.php?t=136605), which required me to download contents of DVD3 from Siemens website. After that, the HMI jumped into life!
Cheers
15 WinCC panel images downloading.jpg 16 Updating firmware.png IMG_20230627_160148.jpg IMG_20230627_161200.jpg
In OB1, I'm monitoring some values (first pic). The values are what I expect. At the same time, I'm monitoring the same values in the DB where...
677
Siemens S7/TIA v16: "Overwrite if object exists online?" HMI loading message... Thus far, I've just been ticking this box, just to get the HMI...
800
I'm having a bad day. Daft question coming up...Anyone know why I can't add anything into this DB? Add button is greyed-out. Thanks
1,637
I imported a customised shape into the project, but I don't know how to actually add into on to a specific HMI screen. Do I use the Graphics menu...
678
Hi I'm trying to display a value on the HMI. In monitor mode on the code, I can see that value, but on the HMI , after downloading, it is...
975