Hi again Gromit.
What confuses the matter is maybe that it is possible with WinCC Flexible.
Siemens entry ID 22255588 describes this in detail.
A downer is that the initial tranfer has to be done via a direct connection.
edit:
There are several other restrictions:
The WinCC flexible engineering station must be connected to an MPI bus or PROFIBUS.
The operator panel on which the transfer is to take place must be connected to an MPI bus or PROFIBUS.
Intermediate routing partners can be connected via another type of bus.
In other words, it is not possible to connect from WinCC Flexible PC, via ethernet, to S7 PLC, via MPI, to panel.