No - nothing unspecified - if you take a look at the attached word document you can see about 10% of the connections for this project - some stations slipped through the net - the hardware config was downloaded with the profibus config , but the rest was not .
We run a policy of never sending a panel to site with software installed , it was only when we had to reconfigure a connection that we realised 3 panels had slipped through the net .
In a recent project I thought we would end up stuck - a 416 processor was the coordinator , and all connections were set up ,ISO over TCP/IP , one network , but we had to add a 317 which wouldn't support an ISO connection - again , this was configured at the 416 end , but left undone at the 317 , but the connection was still good - OK , for good order , we added a standard TCP connection between the 416 and the 317 , but even without , there was a connection established .
Not really a tangent - thread has turned into an interesting discussion on Siemens networking and routing - I've certainly learnt something !