Slc 500 - Bsn - Rio - Pv

If any body can forward me a link of manual for communication between PV+ 1250 and SLC500 CPU 5/04 through RIO.

I will be thankful

Capriconian
 
-- I am trying to configure the RIO in the RSView Studio. But there is no 1747-BSN is not in the scanner list. Can anybody guide me?

-- In the CPU, I am getting short of the instruction memory. How can i increse the memory other than changing the CPU.

-- I need some urgent help. i will be thankful.

Capriconian
 
The 1747-BSN works the same as the 1747-SN from the perspective of the RIO adapter devices, including the 2711P-RN6.

As you know, SLC-5/04 controllers include the -L541, -L542, and -L543 in 16K, 32K, and 64K memory. You cannot expand the memory without replacing the controller with another model.

I again strongly recommend that you seek the local and direct assistance of someone who is familiar with Allen-Bradley controllers and networks.
 
Thanks all for helping.
This time i would like to ask about the simulation of the program.

1) I am using RS-Logix 500 emulate to simulate my PLC program.

2) I read in some of the threads that i can also use RS Emulate for testing HMI application. I tried by adding the driver and the device in the LOCAL Tab. Also i created a shortcut for this device. i am using the Test Application option. But still the application is not getting the values. I dont know where i am doing the mistake.

3) Can RS view ME communicate with RS Emulate? i already have the license.

Thanks & Regards

Capriconian
 

Similar Topics

I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
Replies
48
Views
971
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
Replies
9
Views
773
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
Replies
16
Views
1,362
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
Replies
7
Views
563
After I tried wiring, I used computer program communication to read the PLC N value, but received a NAK signal. And the DL3500 CHA light keeps...
Replies
0
Views
430
Back
Top Bottom