Also - depending on your load size (and how many), it is sometimes cheaper to just get an individual power supply for a couple of units.
Even Allen Bradley & Siemens 1/2A power supplies are usually $50 or less. (usually instruments, HMIs, ethernet switches, etc. fall in this category)
OK super dumb question that I should have asked to start with.
When is a Class 2 Circuit required?
Side Note: How is a fuse not "Power Limiting" :unsure: I feel like I am missing something.
Edit:
Because it doesn't also limit Voltage? meaning it won't protect against voltage spikes?
Edit:
Forgive me if I'm not getting everything right - someone else can correct me.
I believe a fuse does not count because it doesn't actually limit the current. It simply opens the circuit if the current is over a certain point - which it will be for several hundredths of a second (or seconds) before the element melts. A Class 2 circuit won't go over 100W. It is a form of fire protection.
Typically, class 2 circuits are stated as required by the device's installation instructions. I've most commonly seen them on PLCs, HMIs, and most instruments (flow meters, pressure transmitters, etc.)
In this case the answer is simple but not satisfying. If the code doesn’t let you use a fuse to make a class 2 circuit then you can’t do it.
Here’s another reason someone would want a class 2 circuit: “ Components and internal wiring located entirely within a Class 2 circuit are not required to be
investigated”
That means you can put anything in there whether or not it has a listing.
investigated”
Yeah - forgot this is a great one when you need UL / CSA certification. Just use a Class 2 power supply and life is good.
And the above is wrong. Class 2 is limited to 100 ma. Either a class 2 power supply, or class 2 converter. Something like a 1692 ELP.
Fusing doesn’t cut it per UL.
And yes, I often have a class 2 power supply in addition to say a 240W power supply.
Cheers!
Yeah I'll admit it didn't sound like the correct answer to me, but in situations like that, what the UL inspector says is always "right". 🍺
The real issue is in the proof. The section of the electrical code that talks about what can be a Class 2 circuit leads with what can act as a Class 2 power source.
Most of those options are listed devices. If you choose to use a fuse to create a Class 2 circuit the burden of proof is on you to make sure your design fulfills the requirements of a Class 2 circuit. Since you aren't using devices that are already tested to Class 2 requirements that means YOU need to have the testing done, likely by an NRTL.
This is a general truth with UL. You can choose to go off on your own and you may well have correctly engineered a solution that meets the standards. However, the burden of proof at that point shifts to you, not the component manufacturer. That will typically turn into a dollar sign and lots of zeros pretty quickly.
Keith
We normally ground the -24VDC side of a control systems power supply. What are you folks thoughts about grounding the -24VDC side of a class 2...
110
I'm looking for some clarification if anyone here is familiar with UL698a panels. Panel is out of zone/class'd area. with thermocouples extending...
117
Hi, im facing an issue to change the alarm level into another state in the alarm class configuration in Cimplicity. Im trying to change the...
470
Hi - I am searching for an M12 panel receptacles to use for ethernet connections. I see lots of M12 cables that are ATEX / C1D2 rated but nothing...
981
I'm working on getting a handful of devices hooked up to an EWEB card on an Allen-Bradley 1756 PLC using the Ethernet/IP socket interface, and...
2,043