Ultra300i position data via Dnet
Steve Kemp
Nov 2003
122
Hi all.
I've got a connected and very nearly fully working Ultra 3000i servo and SLC500 setup using a DNet scanner. I can home the drive and reset it etc. from the plc. However, whilst I can index it using say, index 0 as set up in Ultraware, I cannot find out how to set the 3000i to recieve position data from the plc. I'm using output assembly #5, and the position data is present at the corresponding outputs. So where's the magic preset lurking?
To alter the Distance of Index 0, you can use Output Assembly 5.
You have to set three different pieces of information in the Output Assembly:
1. In the Command Data Pointer (Byte 3), put the value (133) that correlated to Index 0 Distance.
2. In the Data Value (Bytes 4-7) put the Index 0 Distance that you wish to set.
3. Set the Write Data bit (Word 2, Bit 07). You need to co-ordinate that with the Write Data Busy/Ack bit in an Input Assembly as described on page 2-24 of the User Manual.
I like to set up all this info in an array or UDT and then perform a synchronous copy (CPS) to the Output Data array of the DeviceNet scanner when I'm using Logix. With the SLC, just do it all in one program scan and it will all transfer to the 1747-SDN at once.
I have an array of 55 REAL values. Is there a way to multiply based on the array location ? I have 55 transfer belts that are equally spaced...
154
Hi All, I could do with some advice on a hydraulic control system. It is necessary for me to accurately position a vertical hydraulic ram with...
34
1,916
Hello I am trying to make a program work with a sqo instruction .The process has 5 steps ,and a starting step of zero.There should be 8 sec...
17
1,057
It's been a long time since I've had to think of P&ID tag nomenclature myself (and not gone along with some scheme devised by someone else). I've...
243
Out of interest, I'd like some thoughts on what would be considered best practice with regards to a 2-position turntable control scheme (see...
17
1,149