Scott,
Upon further inspection your problems are as follows:
1. Some addresses don't line up with your symbols in HMI. I would let WinCC-Flex fix this but I would need to Integrate your PLC & HMI projects and make changes. I'm running the most latest HotFix and as such you would not be able to open.
2. The TAG's are showing but you can't see them because of some setting problems (refer to screen shots). You Tags have limits (see tag properties). Once your Tags are out of limits they display in BLACK (see attached) and your text is in Black (see attached) and thus you have tags that are to paraphrase my friends at AC-DC...back-in-black or simply put black on black.
Hope this helps.
Nick
Upon further inspection your problems are as follows:
1. Some addresses don't line up with your symbols in HMI. I would let WinCC-Flex fix this but I would need to Integrate your PLC & HMI projects and make changes. I'm running the most latest HotFix and as such you would not be able to open.
2. The TAG's are showing but you can't see them because of some setting problems (refer to screen shots). You Tags have limits (see tag properties). Once your Tags are out of limits they display in BLACK (see attached) and your text is in Black (see attached) and thus you have tags that are to paraphrase my friends at AC-DC...back-in-black or simply put black on black.