Tuning 1 hydraulic axis with some/many moving as well.

SMOKE

Member
Join Date
May 2006
Location
East and West of Kaos
Posts
475
So some of my hydarulic systems have multiple axes moving in sync. It is easy to tune 1 axis at a time but everything changes when all move. Why can't I tune 1 axis and have the others follow if I agree that I won't crash or they are not liable if I crash them. Synced systems have to move together to tune.
 
There reason why "everything changes when they all move" is that the system pressure drops. The system gain is proportional to the sqrt(Ps*Area-Fl)
where:
Ps is the supply pressure
Area is the area of the piston
Fl is the load force.
Send me a plot or take a screen shot and post it.

Normally when moving at a constant velocity the control signal is constant too. If the system isn't designed right the magnitude of the control signal must be always increasing as the supply pressure decreases.

There are a couple solutions.
1. Install a bigger accumulator.
2. Install a pressure transducer on the supply pressure and run the analog signal to the motion controller. Obviously the motion controller must have an analog input for this. The motion controller can then change the gains on-the-fly as the pressure changes. Actually there is an output scale that was added for this purpose. Few, less than 1 precent, do it though. Most get bigger accumulators.
 
So... Hum what do I do if I have to deal with what I have? I know with fudging I can make it better. To auto tune with all axes moving would do me better than fudging. Money is tight at this time. Even to add AI card since RMC rack is full. And accumulator is out for the time..
Peter the plot shows not enough flow. I have to find a way to equal what is there.
 
Last edited:
It is spelled theory, get a spell check. I use one.

Guess I have to try that. Have you done this with a working sync system? Or is it therorie. Is that spelled correct?

The actuator gain is proportional to the sqrt(Ps*Ape-Fl) where Ps is the supply pressure. Ape is the size of the push or powered side of the piston. FL is the load force. If supply pressure goes down the actuator gain goes down. THe problem is that with only one axis moving the supply pressure is close to the set point but when all the axes are moving the pump will not supply all the oil required until the pressure drops by 200-300 psi. Most pressure compensated pumps only have a proportional gain. How lame is that?
 
Last edited:

Similar Topics

This webinar was held yesterday. I didn't post a link to it. We had over 200 people attend it anyway. There was more question and answers on...
Replies
1
Views
1,217
Is it possible for me to tuning 2 servo at the same time, because this servo is connected by mechanical so I'm afraid that I need to tuning them...
Replies
3
Views
139
Have a logix controller and I'm using the PIDE block for the autotuner. I've got the hang of doing it for direct control things like pressure...
Replies
21
Views
1,769
Hello all, I am using a PowerFlex 700 (Rev 10.001) to maintain tension in a web. We're reading lbs from load cells under one of the rolls...
Replies
85
Views
11,594
Hello, I am attempting to tune a PID loop on a process. The process involves a valve with electronic actuator that has quite a high deadband...
Replies
10
Views
2,193
Back
Top Bottom