Alan Case
Lifetime Supporting Member
Ken. I used the SCIA editor to retrieve the DPI fault of the SMC Flex soft starter.
The returned values were
03 00 00 00 4C 69 6E 65 .???Line
20 4C 6F 73 73 20 43 20 LossC
20 20 20 20 00 00 00 00 ????
00 00 00 00 00 00 00 00 ????????
03 as a fault code is line loss 3.
Trying to retrieve the data with a message block errors with "undetermined error". I think the destination tag type is wrong. At present I am trying an array of 10 Dints.
Version 11 of logix changes the first 2 numbers of my path to "devicenet" ie if I enter 1,7,2,8 it automatically converts to devicenet,2,8
I also tried the SCIA on a powerflex and it returned approximately double the info so I cannot rely on the 20-comm-d manual for the structure of the return.
When I get a bit more spare time I will research more. Regards Alan Case
The returned values were
03 00 00 00 4C 69 6E 65 .???Line
20 4C 6F 73 73 20 43 20 LossC
20 20 20 20 00 00 00 00 ????
00 00 00 00 00 00 00 00 ????????
03 as a fault code is line loss 3.
Trying to retrieve the data with a message block errors with "undetermined error". I think the destination tag type is wrong. At present I am trying an array of 10 Dints.
Version 11 of logix changes the first 2 numbers of my path to "devicenet" ie if I enter 1,7,2,8 it automatically converts to devicenet,2,8
I also tried the SCIA on a powerflex and it returned approximately double the info so I cannot rely on the 20-comm-d manual for the structure of the return.
When I get a bit more spare time I will research more. Regards Alan Case