I am trying to install a 1756-HSC/A card with a 24vdc encoder, and I downloaded the sample code from Rockwell. I have connected external 24vdc and common to the AIFMCE4 (1492-ACABLE-XA) and then connected that power to the encoder.
I programmed the generic ethernet card, added the data types and the programming, and I am getting no response on the HSC_IN channels. I have looked at the pulses with an o-scope to verify the signal is transmitting to the card.
I am not sure I understand the programming as to intialization and feedback. I am not getting the ABZ LEDs on the front of the card. I can toggle the Output LEDS, but that is it. Any help is appreciated.
If you can measure the correct voltage and commons at the correct module terminals, then I think you should see lights, but perhaps only if the card is enabled.
zip and post the code if you can, a snapshot of run mode.
What sample code have you used when configuring the high speed counter module?
Using a 1756-HSC module within a RSL5K application is similar to any other type of 1756 hardware; the 1756-HSC module's profile is part of the RSLogix 5000 installation package and the Generic Module configuration should not be substituted to the already available 1756-HSC one.
Visit http://literature.rockwellautomation.com/idc/groups/literature/documents/um/1756-um007_-en-p.pdf
Starting with page 59, the procedure of adding a high speed counter module to an RSL5K project is in-detail explained.
I have am trying to determine if I can use a 1756-IB16I (or some dc input equivalent) to handle a 24vdc input pulse frequency of 80 pulses per...
959
Just finished an upgrade from a SLC500 to CLX where they had a 1746-HSCE and we're now using a 1756-HSC. Two wire pulse signal from the...
1,313
I have an older SLC500 that has a PLS card in its rack. I want to remove the SLC and add a L23E-QBFC1. Can a resolver be wired up to the High...
1,696
Our ABB Vision System requires a Pulse Train Input from an Encoder (12-15 VDC)to calculate the speed of the web. Instead of adding an encoder to...
1,576
I am upgrading HSC modules and have some questions. I can't attach the manuals for reference as they are too large. 1746-HSCE uses M0:e.1/4 for a...
1,661