I have a 1769-HSC card connected to a CompactLogix and using RSLogix 5000. I have device simulating a pulse to the card. InputStateA0 is showing up as 0 then 1, then 0. The problem is that no current counts or stored counts show up.
This is my first time configuring one of these HSC cards. I've attached screenshots of my config. I've tried changing a bunch of configuration settings, but am not getting any different results.
I appreciate any suggests. Thanks.
Haven't used these modules but check tag
Local:"YOUR CARD SLOT":O.Ctr0En it should be set to 1 I believe
seems odd that the enable is in the output array but from what I read that's how she goes
Exactly. The use of the output lets your program start and stop counting as needed.
Secondly - if, during runtime within the program, something in the configuration area must be changed then you must follow this order.
1. Stop counting (CtrxEn = 0)
2. Change the configuration area value
3. Issue a 'Module Reconfig' message
4. Wait for the message to complete without error
5. Resume counting (CtrxEn = 1)
Hello All, I am just trying to learn up on these modules, as I installed my first last week. The intent is to use this module for 3 pulse flow meters. Hopefully, I have selected the right card for the job and have it wired correctly.. I have a couple questions and wasn't sure if I should start a new thread or post the questions here.. Let me know before I post the questions. I was unsure as far as how to wire and setup for reading flow in GPM
Thanks in advance
Hello all. I am having trouble setting up my HSC to count pulses from a prox switch. I have it wired to the prox and I see the .InputStateA0...
1,378
Here is my hail Mary pass I have a wheel that produces 33 pulses per revolution. The RPM of that wheel will be anywhere from 25.21 to 62.7 Pulses...
4,709
Hello all. I have an issue that keeps plaguing me. The system has a 1769-L24ER processor and a 1769 HSC card. I am using CH.0 for tracking...
1,472
Hello, Im trying to use a 1769 HSC card to get the RPM of a single channel encoder at 60ppr. Ive read the other threads of people have similar...
1,698
Flashing Red OK Status indicator : Rockwell Automation Publication 1769-UM006E-EN-P - July 2013 Table 23 - Configuration Error Codes pg 117...
2,184