I was given a AB 20 I/O PLC with a hand held programmer to build a trainer.
I've been messing around with the programmer and can not insert bits into the ladder program: Every time I try to add an bit instruction I get the message "File cannot be created". I have tried various addressing and still not luck.
I can add timers with no problem, but when it comes to I1: or O0: addresses I get the error message.
I have a 1747-L20L AB brick and a 1747-PT1 ser.A HHT
I am only using the built in I/O on the PLC
inputs 0-15
outputs 0-7
When I try to add a XIC or XIO I am using the address I1:x/x (the unit then formats the address to I1:X.X/0
The same thing with trying to assign outputs: O0:X/X etc.
I have searched the pdf for the HHT for the error code and have found no mention of it. I have looked through the PDF for the PLC and still nothing, and the AB SLC 500 reference doesn't give me any information.
Since I can add timers to the ladder (using the T4:X format) I believe there is something in the addressing that is not allowing the PLC to assign the bit to either I/O.
Thanks o_O
Why are you putting a number before the colon? For inputs and outputs, you don't use the data file number like you do for the other registers (B3:, T4:, etc.). As lightning said, try I: instead of I1:, and O: instead of O0:
I haven't used an HHT in Y-E-A-R-S!... :D
-Eric
You are aware that the I Inputs and O Outputs are fixed and you are not able create them by adding more.
Although you should be able to use XIO or XIC with the existing set of inputs and outputs that the 1747 L20L has
Try this an see if it works
Try B3/0... B3/1... etc as the bits and see if you can add them
Found it, the proc was the wrong setting. Once I got it to the right proc setting it made all the difference in the world.
The battery in the HHT is dead and so each time the unit turns off the select-processor (SEL-PROC) setting changes back to the default model. Basically I was focusing on the wrong end of the problem; it couldn't create the file because the processor unit on the plc didn't match up with the processor selected in the HHT.
Hello, I use a Siemens Sinamics G120C inverter in combination with a S7-1200 cpu. I use the Main Setpoint with the Providrive option and send...
756
Hiya, I have a project coming up using a unimotion servo linear actuator with a Schneider PLC (tm251) Are there any blocks available in the...
969
Does anyone know of a free program I can use to upload the program from an AB SLC 500 Fixed and read the error code? I don't want to do any work...
1,587
I am looking for a standalone (no PLC required) servo drive that I can set up to follow an incremental encoder at a fixed ratio AND will allow me...
5,026
I am needing to connect a fixed style SLC-500 to an ethernet network for data collection to an OPC Server. I see the Fixed Style SLC-500 has an...
2,582