I have a problem with AI module (1756 IF16) error (module fault: 16x0009, additional fault code:16x0001). Explanation for the error is:
0x0009 ==> The configuration for the module is invalid. The module configuration may have been changed in the data monitor or programmably. Verify that configuration is valid by using the module configuration software to validate your configuration.
16x0001 ==> configuration of the I/O module is not synchronized with another configuration owner (controller) or an invalid reconfiguration procedure detected. Check that all controllers for this module have the same configuration.
The fault code discription is really good b iu dont know how to resolve this problem. When i try to load configuration (from rslogix 5000) on my secondary controller i recieve error message: Failed to modify module properties. Operation is not alowed to a synchronized secondary.
I must say that i am remotely connected to online redundant controllers (5563) so I don't have physical access to modules. On FactoryTalk SCADA I recieve the data normally, but it's highlited because of diagnostic involved with visual aspect of tag representation.
0x0009 ==> The configuration for the module is invalid. The module configuration may have been changed in the data monitor or programmably. Verify that configuration is valid by using the module configuration software to validate your configuration.
16x0001 ==> configuration of the I/O module is not synchronized with another configuration owner (controller) or an invalid reconfiguration procedure detected. Check that all controllers for this module have the same configuration.
The fault code discription is really good b iu dont know how to resolve this problem. When i try to load configuration (from rslogix 5000) on my secondary controller i recieve error message: Failed to modify module properties. Operation is not alowed to a synchronized secondary.
I must say that i am remotely connected to online redundant controllers (5563) so I don't have physical access to modules. On FactoryTalk SCADA I recieve the data normally, but it's highlited because of diagnostic involved with visual aspect of tag representation.