I am a plc rokie, I can only understand simple ladder logic and I would be grateful to learn more from you guys. Anyone can explain to me anything about analog input/output and how the data being manipulated in the program? Any help would be appreciated.
what exactly would you like to know?
in general, you basically wire voltage source, let's say ultrasonic sensor, (for example 0-10V), or current source (for example 4-20mA) to the PLC's analog input and each scan (or right from the any part of the program in some cases in some PLC brands) you have a variable(or memory area) with the value proportional to the voltage/current level.
and the same story with analog outputs, you just write the value to the variable and get a proportional level of the voltage/current from the analog output...
the most important difference from the digital I/O is that you dont just have 1-bit signal, but do have something like 12-bit value
For example, if you use Step7 to program, The analog input is a word and designated PIWxxx ;xxx=word address
The analog output is PQWxxx
The word addresses is defined in the hardware configuration.
usually, the analog value inside the PLC is in a range (example: from 0 to 27648) which corresponds the physical value (example: 4-20mA), Where 0->4mA and 27648->4mA
You have to scale your output or input with the value inside the PLC.
Example:
you have a level sensor from 0 to 100m
You then need to scale the range (0 - 27648) with the physical value (0 - 100m)
Then you use scissors multiplication to get the value as follows:
Physical -> PLC
0m -> 0
100m -> 27648
Ym -> X
then Y=(X * 100)/27648
Where: X is the input from PIWxxx
Y is the distance in meters
Thanks a lot mr girevik.
I am sorry, i posted a very vague question that you found it hard how and where to start answering. Anyway, at least I learned from you guy the basic principle of analog input/output. If it's ok with you, can you send me a sample configuration of analog input/output (ex. temperature or pressure controller) and its plc program (a ladder diagram)using mitsubishi plc. Thank you very much guy.
Thanks Mr. Amazingahmed.
I now got a clearer picture on how to use analog signals. I guess its just a matter of studying more and putting it into practice. Thanks guy, you help me a lot.
Hi, I tried today to get RD3A and WR3A instructions to work on the PLC and it didn't work, but it worked in simulation. I followed the clone...
18
1,465
Hello, I have a small programming task that I need help solving. I have to: * Create an analog input (4-20v)and a digital output * The analog...
45
25,231
Hey guys, running into issues trying to get some analog input and output cards for customers needing a few points here and there. with that in...
4,937
Hi; I need to monitor and log the 3phase AC input voltage for which I need a device to convert AC input voltage (say 350 - 440V) to analog (0-10v...
1,383
Greetings, I have been charged with a project to link data from a Beckhoff PLC using Allen Bradley Point IO to a PLC 5. The PLC5 does not have...
4,073