Ours have to be rest every time the lines gets restarted or a e stop gets pushed and then we have to push the PU button and then run again I can't seem to find how to adjust it so it wont need to e reset so much.
Most likely your motor is too small for the load and the VFD (inverter drive, same thing) is protecting the motor from thermal overload. That's why it is making you wait before restarting it, it is forcing you to let the motor cool off. It's also possible that the VFD is not properly set up for the motor, the application, or the environment. There are likely fault codes that are being displayed on the VFD, you need learn what they mean.