The auxiliary encoder inputs on the servo are differential. The 'Tie' terminal should be jumpered to the A- and B- inputs when you're connected to a single-ended signal. You should also tie the servo's DC common (pin 14) to the AD's DC common even if you don't use the servo's 5VDC supply to power the AD's pulse output.
The CW/CCW mode means that a pulse train at the A terminal will command motion in one direction and a pulse train at the B terminal will command motion in the opposite direction. I repeat, I know nothing about the AD module, so in my ignorance I'm going to suggest that you make sure you're not outputting an A quad B signal from the AD module.
To make sure your configuration of the servo is correct, try connecting/disconnecting the servo's +5VDC to the A input to see if you can generate any motion. You may have to set a fairly high master/slave ratio to be able to observe much motion from a single pulse.
I do not know the hardware you're talking about, but on other setups, I have seen simular problems a number of times.
As a couple of people here suggests, the signal level(s) are not read correctly. Either its due to a tie problem as suggested or a signal level problem.
With an oscilloscope you can monitor the signal and verify that the duty cycle for the signals are 50/50. Most puls inputs will accept some variation, but not too much (gets more critical as frequency increases). Furthermore, with the oscilloscope you can monitor that the logic "1" input has a level that is read as logical "1" by the drive. As with the logic "0".
If levels are not reached, which is a very common problem, you need to tie up (logic "1") and/or tie down (logic "0").
e.g. Single ended inputs, problem with logic "0" signal level:
Tie down logic "0" by inserting a 1k ohm (5V signal level) or a 2k ohm (12V signal level) resistor between signal A+ and A- (which then is connected to common, which in turn is connected to ground). Do the same for B channel.
Kindly, has anyone tried to control Lenze servomotors with Siemens S120 drives ? Any special hints ? Have some concerns for the resolver and servo...
236
I am trying motor startup with pf525 drive by using wizard start over ethernet communication but during direction test it's showing control error...
191
HI using a G120 sinamics i used the Profidrive in order to control the position in the picture i showed how my system is ,alos how i set the...
1,071
Hello, I am trying to get a 32MV4341 Lenze AC Tech VFD running a conveyor to be controlled by a 24VDC photo eye on the nose end of the conveyor...
1,933
Hi Everyone am controlling a stepper motor with 1215 plc, when using motion control(V6/7) you don't have any option of using HSC as feedback is...
913