Rob
PV Plus Takes up 6 connections but as far as performance you also have to thinking about IO PPS and HMI PPS which the HMI PPS changes depending on how many tags the HMI is processing and how fast (RPI).
UDT to pass the dta in your case would most likely be best.
You can use the stratix 6000 as long as all 3 pieces of equipment are going to be on the same logical network (Subnet).
If keeping 3 seperate networks you will need layer 3 which requires the stratix 8300.
Also make sure that if you have multiple switches the IGMP Quirier is only active on the switch with the lowest IP Address.