Media Redundancy on Profinet (Siemens PLC)
userxyz
May 2002
any
2,768
I have a problem with Media Redundancy.
My config in test is like this:
When I disconnect 1 side, the red lights goes on and the slave is lost.
This is a test set-up, because on a project where I have 5 slaves and I wanted to have media redundancy, after a powerbreakdown the network does not reconnect it slaves, only when breaking the ring the slaves become online again. The media redundancy does not work for me at the moment..
Anyone with some redundancy experience here ?
Thanks in advance,
Regards,
C
1 step further after configuring a topology
I've red that a topology has to be draw in the hardwareconfig, so I did. Then redownloaded the HW.
Here the diag after disconnecting a cable:
The thing is, when I disconnect the cable between ports 1 and 1 the EXTF red light is on, but no BUSF, if I disconnect the cable between ports 2 and 2 then I also get a BUSF for some seconds.
The remote IO is lost when braking a connection, so I think it still fails to work.
Any ideas ?
I've never tried to use MRP with only two devices, but I assume it should work.
I see the "Wrong Partner" statement in the HW config. Does your real wiring actually match the offline topology?
it does
Yes it does.
I placed an output card (8 Q) and I connected MB0 to QB0. MB0 configured as clockbyte in the cpu. This way I can verify the output signales.
I can see that breaking one side shuts off all outputs for 5 seconds... same result asif I would not configure media redundancy...
:confused:
What version/type of ET200 are you using? I think some versions are unable to function as nodes in a MRP network.
Pi
I just wish to clarify how the panel LEDs react when a cable is disconnected:
When both are connected: solid for the RUN light, no other LEDs on
When you disconnect P1, P2 still connected: EXTF and RUN solid, no others on
When you disconnect P2, P1 still connected: EXTF and RUN solid, BUSF flashing
Do you lose I/O signals in both cases or just one?
Is this correct?
Pi
leds
One side stays good, other side red blinking and green blinking, outputs become low, so connection falls away on 1 side.
Is this correct?
Pi
Are you able to monitor the ring status online as you connect/disconnect cables? There should be an option to monitor topology status online. It looks like the MRP is configured correctly, but it's not connecting through the redundant port.
Try swapping your cable connections. If the cable was connected to port one, move it to port two. Does the problem with losing outputs follow the cable?
Pi
I am setting up my first ring with siemens. There are two manager roles to select. "Manager" and "Manager (auto)" What is the difference...
1,467
I am looking for a fiber-to-copper media converter that is 120 VAC powered with terminals for placement in a small panel, so I can't use the wall...
147
Hallo, Please, I would like to ask that ETAP1F can be used as a media convertor from fiber to copper and copper to Fiber in DLR? I have attached...
678
Well, I called RA support today to try and get the installer for RME, and to my surprise they claimed they no longer had the install files (I know...
23
2,260
I am using factory talk view studio site edition Version 8.20.00 . In that I added one media player to play video. But I cannot play it...
1,068