ML1200 comms fault to io modules
James Mcquade
Oct 2007
Nashville, Tennessee area
3,683
Hi all,
i have a customer that shuts the power off to the plant several times a year to do work on their substation, consequently all plc's power down as well.
when power is restored only the AB ML1200's give them a problem. the plc faults out because it looses communications with the expansion i/o modules 99% of the time.
i suggested that they set ststus bit S:1/8 - fault override at power up since i have had to set that bit on several slc 500 units.
the software (rslogix 500 ver 5.50.00 )gives an error an won't let us set the bit, it says the bit is not writeable.
it it my customers software version or is this truely a read only bit?
thanks in advance,
james
G'day forum! I'm running a 1762-L40BXB (MicroLogix 1200). My issue today is that when I connect using my serial cable (Works on a 1000 and 1100)...
2,710
I have a ML1200 with 2 serial ports. Channel 0 is configured for modbus communications with a motion controller. The programming / HMI port is...
1,834
I need to connect a 2711 k6c9 panelview to a ML1200 PLC. I do have a spare 1761 cbl pm02 cable. What do i need to do to this cable to get the...
2,848
Hey all! Long time reader, first time poster! I have an EA9-T7CL and an MicroLogix 1200 connected via DF1. I'm all good and got everything mostly...
652
Hi every master,Recently i met a fault about 1762-L40BWA 1,When i get the PLC, The Fault light is lighting, I am not remember the fault message,I...
718