raul_vaze Member OP R Join Date Feb 2008 Location mumbai Posts 87 Jul 28, 2008 #16 Andrew i can ping the micrologix quite easily and as suggested i did put all the things mentioned in ur email . When system goes into the runtime i always get a hardware alarm " PLC server I/O device offline" ??????
Andrew i can ping the micrologix quite easily and as suggested i did put all the things mentioned in ur email . When system goes into the runtime i always get a hardware alarm " PLC server I/O device offline" ??????
kellian Member K Join Date May 2002 Location Capella Posts 155 Jul 28, 2008 #17 Can you post a screen shot of your communication configuration Port, Board, IOdevice
gimenes Member G Join Date Feb 2012 Location Brazil Posts 1 Feb 9, 2012 #18 Have you tried shutting down RSLinx? Worked for me. (Using same serial cable for the communication with RSLogix and CitectScada7.2)
Have you tried shutting down RSLinx? Worked for me. (Using same serial cable for the communication with RSLogix and CitectScada7.2)