Glenn,What is your rationale for going to a PLC ?
....which have to come on at particular times for particular time periods.
gets my voteLook at the Automation Direct CLICK PLC
The Click (and many other brands and models) can handle all of that. Cost may be an issue, so shop carefully and buy only what you need. Do not buy a 2-amp PLC output to handle a 2-amp AC solenoid valve. Get at least 2 times the solenoid running current to allow for the initial in-rush current. Otherwise you will burn out your Output module.Here's what i'm lookin at: 12 outputs, individually programed to handle 2 amp 24vac, 2 motor starter relays that have a relay coil compatable w/ what the plc output for the coil relay activation, real-time capabilities, and a few inputs externally powered matching the input range of the plc card.
If you buy PLC relay output modules, then you can use nearly any AC voltage to power your external relays. PLCs allow you to choose the voltage that you apply to the PLC relay. You just need to choose an output module that has a range that covers all the voltages that you need to use. Many (including the Click) have a range of 12 to 264 volts AC that can be applied to the PLC relay output coils and contacts....2 motor starter relays that have a relay coil compatable w/ what the plc output for the coil relay activation,...
What is your rationale for going to a PLC ? If you just want to control the pumps with switches, hard-wired relays may be cheaper. Once built, the PLC system would be easier to modify or adjuat by editing the program.
i think getting dc voltage added into the equation is a waste of time and money. [K]EEP TIMPLETUPID lol. id get a 120vac plc,
Yes this system is for my back yard.
Yes, maybe a waste, for you, me, electricians, and others.
But what about for Danl? I hesitate to recommend 120 volt equipment (bare 120 volt terminals can kill, adults, pets, and kids) without knowing the skill level and knowledge of the recipient. Based on his questions, and planned use, maybe yes, maybe no.
Great, it is good to know that you know what you are doing. Is there anyone else living in your house that could put their fingers across the 120 volt exposed terminals of your PLC? Is there any need to install your PLC into a cabinet or a locked closet? We electrical types often forget that the the only thing the next guy/girl coming into the room knows about electricity is how to turn on a light switch. Make it safe for all who will be exposed to it. Enough said on that.It's ok guys. I'm a tech. I've wired all kinds of stuff.
Doubtful, but possible if you use some of the Click Isolated Relay 7-AMP Output modules for your heavy current users, and the normal 1-Amp built-in outputs for the low-current loads. Remember, the Click relay outputs do not take their power from the PLC. Instead, they take power from your power supply to the output module terminals (whether it be 120 volts or 24 volts). The Click output relays simply have to have contact ratings to handle the connected load. This has nothing to do with the internal power rating of the PLC CPU. There is a maximum current rating for all the outputs on each module (due to the limited total heat dissipation of the module).Seeing that the click system is limited in output amps, it is doubtful that this or any other system would have an output rating to power as many solenoids up at the same time as would be required by my application...