The outputs (6) on the plc are strictly 24 vdc @ .1 amp per point. I'm not sure how this would handle an inrush at the valve solenoid though. Maybe another relay block?
NO! NO! NO! I will say it all again. You need to adjust your thinking about how PLCs work. I think you are under the impression that PLC outputs must be the same voltage as the power supply that operates the PLC. That is not true AT ALL. PLCs are made to be very flexible. In the case of the Click, the power that supplies the Click CPU power must be 24 VDC. But the power that supplies the relay outputs does not have to be 24 VDC. The outputs on the Click C0-01AR-D are NOT strictly 24 VDC. They are relays, so the output voltage can be nearly anything, AC from 6 to 264 volts AC, or even DC from 6 to 27 volts DC (see attached picture of the C0-01AR-D specifications).
http://www.automationdirect.com/adc...s_(Stackable_Micro_Brick)/PLC_Units/C0-01AR-D
1. Buy the Click C0-01AR-D.
2. Buy a 2-Amp, 24 volt DC power supply to run ONLY the Click CPU.
3. Buy a 120/24 VAC transformer to run your 24 VAC solenoids.
4. Buy two 7-Amp isolated relay modules to get your outputs up to the 12 that you need. You can run your two pumps and some of your 24 VAC solenoids from these add-on auxiliary modules.
Connect the 24 VDC power supply to your Click power terminals. That is the only place you need to use the 24 VDC power.
Connect the 24 VAC from your new transformer to one side of your Click relay contacts. Connect the other side of the relay contacts to your solenoids. Now when the Click program turns on the outputs, 24 VAC will flow to your 24 VAC solenoids.
Forget about using 24 VDC on your solenoids. You do not have to, so why would you? Like others said, that is a burn-out waiting to happen.