Dear All
Can any one help me for modbus communication between
S7 200 CPU 224XP and PID temperature controller having serial port.My aim is only write temperature SP and read Act Temperature
What I have do
1. Connect temperature controller to PLC port 0
as
PLC PORT Pin Temp Controller
3---------------------------------> RS 485 (N)
8---------------------------------> RS 485 (P)
But now i am confused for
CPU 224 XP configure as Modbus master or slave mode?
Pls help me for the task
Also if anybody has sample project pls send
I have Modbus library installed with Microwin 4.0 SP5
Here is attache temperature controller manual
On the PID500 controller side,
Holding Tegisters will have the setpoint and the process variable. Holding registers are in the 4xxxx address range. The document doesn't show the leading 4, but it's 'understood'.
Holding register address 40021 appears to have the setpoint, mysteriously labeled 'zone setpoint 1', probably as a signed integer value, given its range of -1999 to 9999.
I'm perplexed about what they call the Process Variable (actual temperature). It's pretty obtuse to not have a Process Variable (PV) right up front in the map.
Maybe holding register 40003 is the PV because I'm speculating that in the absence of something clearly labeled "process variable" 40003 might be the PV, even though the term 'Resolution' appears for 40003. Resolution is probably intended for 40004 but the table is misprinted and where it says 'Resolution' it should say 'Process Variable'?
Or maybe holding register 40007 aka "Display value scaling point", ranged of -1999 to 9999 is the PV?
Likewise, these 'maybe' PV's are probably signed integers.
Sorry, I can't help you on the Siemens side, other than the Siemens must be a Modbus Master. Modbus slaves cannot talk to one another.
Hi all, Currently having trouble getting a speed reference to write over modbus to an Omron M1... I can successfully write a run command and...
284
can i send and recieve data using my yokogawa UT35A controller with my siemens s7 1200 plc using profinet communication without using gsd file
399
Hello all. I am trying to read out the values from a Carlo Gavazzi EM340 energy analyzer via Modbus communication. The S7-1200 PLC has the CB1241...
29
3,846
Hi, a customer has an installation on which a Yamatake DCS monitors about 60 Rosemount FF temperature transmitters. The DCS is a Mobdus RTU master...
585
Hello All I have a modbus tcp device(Julabo magio) with an DB9 pin assignment. Pin3=B and Pin8=A. I would like to connect it on the secondary...
1,634