siemens s7-300 and Lumberg I/O Module

Avatar_41

Member
Join Date
Aug 2019
Location
Istanbul
Posts
96
Hello. I have Cpu 315-2pn/dp and I have Lumberg 0970 PSL 701 DI/DO Module. I uploaded the GSD file, but I could not communicate. I think my cable connections are wrong. Can you help me?
 
The cable connection is very simple.
If there are only the 315-2PN/DP and the Lumberg device, then in the Profibus connector on both ends:
Green wire goes to A1 and red wire goes to B1.
And in both connectors the termination should be set to "ON".


The only thing that must be set up in a Profibus slave is the station no. Usually it is done by dip switches. Have you done this and does it match the setup of the slave station no in the STEP7 project ?
 
And if they are feed through connectors make sure the cable is attached to the IN terminals and not the OUT terminals.
 

Similar Topics

Hello all. I have an ESA HMI that is connected to a Simatic S7-300 (CPU312). I have uploaded the program from the PLC which is written with Step7...
Replies
6
Views
1,450
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
Replies
3
Views
692
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
Replies
2
Views
1,070
G'day guys, I am setting up a s7-300 as a test rig for the workshop and when I downloaded the PLC is not going into run mode, I keep getting a...
Replies
35
Views
5,230
I am trying to write just MSEC to S7 300 Controller date/time using OI.SIDIRECT Aveva communication driver? The old HMI (WINCC) tag is assigned...
Replies
1
Views
1,061
Back
Top Bottom