I'm working on a project using SM331 2AI board (6ES7 331-7KB02-0AB0).
Describing the hardware, the SM331 is connected on a remote module IM153-2 that is connected by profibus to a S7-400H through a Y-Link device. I have no errors (SF LED). On the analog input it is connected a ultrasonic sensor with separated power supply and according Siemens manuals it is a 4 wire connection, so the SM331 is configured for a 4 wire 4..20mA connection (on step7 and on the board shunts).
I already measured the current with a multimeter, and the analog signal arriving to the board is correct and according the ultrasonic measurements and on S7-400 I'm always reading -32768.
Electrically, the board is wired according the attached file. On this equipment (where the remote module is mounted) there is no "functional ground" so the terminals 3, 5, 10 and 11 are connected to 0VDC. As I'm using only channel 0, terminal 4 and 5 are shunted.
On the step7 hardware configuration, the parameters are as the attached image.
Does any one have some ideia about to solve this problem
Thanks for your help
Best regards,
Renato.
Hello Experts, I need your help about this issue of mine about my Siemens Analog Input Card SM331 having SF LED lit. I know this is system fault...
4,492
Hello All, Want to know what should be the correct setting for the Measuring range for connecting this instruments to my AI Card? So I am...
2,400
Hello Experts, I am going to be integrating an AI module into an existing panel and wants to know what should be measuring range setting when i...
1,887
Hello guys, I have a thermocouple with a green wire which measures a temperature 0-1100 degrees. I dont have any information, only the color of...
7,162
I have gradually been selling off some old stock of Siemens S7 PLC modules. I have had an enquiry. The customer wants a 6ES7-331-7KF02-0AB0 I...
2,741