Simatic touch panel with profibus comms
ThePortLion
Oct 2007
Ireland
58
Hi guys
I want to upgrade the hmi on a stand alone system.
Currently I have a pc running intouch v7.1 talking
through S7 IO server software to an siemens S7313c
plc over ethernet. The pc display is a 15" touch screen.
I want to modify this configuration to a 15" Simatic panel
pc talking directly over profibus to the plc, thus removing
the standard pc from the equation.
Basically what i need to know is, are there any pitfalls
that i'm not seeing? I ask because these simatic panel pc's
are quite expensive.
Is there any extra Step7 software required to configure the
panel? I'm currently using Step7 V5.3 + SP3
Can i keep the intouch application (it's quite small) and
still use profibus or do i have to rebuild it in something
like Protool?
Any pointers would be appreciated.
There aren't any particular pitfalls as such, other than the price, which as you mention isn't exactly cheap.
Unfortunately the same applies to WinCC Flexible which you will need in order to program the panel.
The regular 313C does not have profibus, only MPI on board.
You can use an MPI connection or an ethernet connection (I suppose that there is a CP343-1 in the rack).
I dont understand why you want to switch away from ethernet to profibus.
Thanks guys for the responses.
The reason I want to get rid of the standard pc is that
the area it works in gets quite hot and I'm frying pc's.
I'm using Intouch 7.1 which isnt supported in windows XP.
I have got it running on xp alright but I cannot get the
s7 io server software to run in xp. The pc presently runs
Win 2000 Pro.
The new siemens panel pc's, obviously, dont have Win2000
support. Not to say it wouldnt run okay but it might be an
expensive risk.
Therefore, from my limited knowledge, :oops: I thought that
i could maybe talk directly to the plc using an
industrial spec siemens panel.
Thanks Jesper, I'm only now realising that, yes, the 313c
does not have a profibus port. I have an ethernet cp, yes.
So is Wincc the only option?
No there are many many options.
Surely Intouch may also exist in a newer version that support Windows 7. And an IPC rated for hight temp should be possible too.
A Siemens touch panel that connects via MPI or ethernet is a rugged solution.
For Siemens OP/TP177 - OP/TP277 - Compact panels, you need WinCC Flexible 2008 Standard.
I like the new Comfort panels. They are much better than the older panels and less expensive too.
For the Comfort panels you need WinCC Comfort v11.
have you gave a look to the siplus line of hmi that support lower and hier temp...making the move you may consider that too
I strongly support what Jesper said. Keep the Ethernet CP, and continue using the Ethernet link. Get rid of the PC, and use a better Simatic HMI.
You'll need to redesign the screens using WinCC flex in any case.
MP377 is a good option with it's 12" screen. Mp277/TP177B will work also. But the smaller screen sizes of these panels may pose some challenge, if the original PC app used very detailed graphics.
KTP1000 would be a nice choice. This display and the software (Simatic Manager 10.5) are much cheaper.
How Does a Touchscreen Work?
http://http://www.njytouch.com/view.asp?keyno=647
A basic touchscreen has three main components: a touch sensor, a controller, and a software driver. The touchscreen is an input device, so it needs to be combined with a display and a PC or other device to make a complete touch input system.
1. Touch Sensor
A touch screen sensor is a clear glass panel with a touch responsive surface. The touch sensor/panel is placed over a display screen so that the responsive area of the panel covers the viewable area of the video screen. There are several different touch sensor technologies on the market today, each using a different method to detect touch input. The sensor generally has an electrical current or signal going through it and touching the screen causes a voltage or signal change. This voltage change is used to determine the location of the touch to the screen.
2. Controller
The controller is a small PC card that connects between the touch sensor and the PC. It takes information from the touch sensor and translates it into information that PC can understand. The controller is usually installed inside the monitor for integrated monitors or it is housed in a plastic case for external touch add-ons/overlays. The controller determines what type of interface/connection you will need on the PC. Integrated touch monitors will have an extra cable connection on the back for the touchscreen. Controllers are available that can connect to a Serial/COM port (PC) or to a USB port (PC or Macintosh). Specialized controllers are also available that work with DVD players and other devices.
3. Software Driver
The driver is a software update for the PC system that allows the touchscreen and computer to work together. It tells the computer's operating system how to interpret the touch event information that is sent from the controller. Most touch screen drivers today are a mouse-emulation type driver. This makes touching the screen the same as clicking your mouse at the same location on the screen. This allows the touchscreen to work with existing software and allows new applications to be developed without the need for touchscreen specific programming. Some equipment such as thin client terminals, DVD players, and specialized computer systems either do not use software drivers or they have their own built-in touch screen driver.
Touchscreens Add-ons and Integrated Touchscreen Monitors
We offer two main types of touchscreen products, touchscreen add-ons and integrated touchscreen monitors. Touchscreen add-ons are touchscreen panels that hang over an existing computer monitor. Integrated touchscreen monitors are computer displays that have the touchscreen built-in. Both product types work in the same way, basically as an input device like a mouse or trackpad.
Touchscreens As Input Device
All of the touchscreens that we offer basically work like a mouse. Once the software driver for the touchscreen is installed, the touchscreen emulates mouse functions. Touching the screen is basically the same as clicking your mouse at the same point at the screen. When you touch the touchscreen, the mouse cursor will move to that point and make a mouse click. You can tap the screen twice to perform a double-click, and you can also drag your finger across the touchscreen to perform drag-and-drops. The touchscreens will normally emulate left mouse clicks. Through software, you can also switch the touchscreen to perform right mouse clicks instead.
SIMATIC TP177B
General touch panel, meet all kinds of application ROFINET or PROFIBUS DP environment.
Outstanding features:
performance
-performance could be compared to today's 270-6"
-2 MB user memory, replacing the previous 768 KB
Easy to use
--5.7 "STN blue level 4 grayscale display
-reliable, low maintenance
-integrated, there are all kinds of interface
--5.7 "STN colour display (256 color)
-the volatile, free maintenance alarm buffer (without the battery)
-color type support Sm @ rt Service, Sm @ rt Access
-look smooth (IP 65, EX 2/22)
Flexibility good
-universal
-32 kinds of project language
-five languages online switching (including Asia and Cyril language)
-built-in USB interface (for the printer and download, etc)
-standard multimedia card slot
-color type belt "Profinet I/O" Ethernet interface
-by NEMA4, Ex2/22, classification authentication
-use WinCC flexible 2005 or more efficient configuration
SIMATIC TP 177 B DP mono
SIMATIC TP 177 B 4 Inch Widescreen
SIMATIC TP 177 B PN/DP color
SIMATIC TP 177 B PN/DP color INOX
General input device, meet all kinds of application environment PROFIBUS DP.
-5, 7 inches STN display
-four blue hue
The 320 x 240-resolution
-Windows CE certification
-PROFIBUS DP interface
-2 MB user storage
-strong plastic shell
-protection grade
The front panel IP 65, NEMA 4 x, NEMA 12
Back panel IP 20
-WinCC flexible or more efficient use of configuration
-the front panel size 212 x 156 mm (wide x high)
--install the size of holes 198 x 142 mm (wide x high)
-equipment installation depth 45 mm
Color input device, small size, combined with touch function and function keys to meet the PROFIBUS DP or ROFINET various applications.
--4.3 inch widescreen display
--256 color color
The 480 x 272-resolution
Background-LED light can be adjusted 20%-100%
-touch screen
-four extra can touch buttons
-PROFIBUS DP and PROFINET interface
-through the touch screen and function keys of PROFIBUS DP or or PROFINET IO interface
-2 MB user memory
-SD/multimedia card combination slot/USB interface
-protection grade
Back panel IP 20
-use WinCC flexible 2008 or more efficient configuration
-the front panel size 140 x 116 mm (wide x high)
--install the size of holes 123 x 99 mm (wide x high)
48 mm depth--installation
The colour of general input device, meet all kinds of application ROFINET or PROFIBUS DP environment.
--256 color color
-touch screen
-2 MB user memory
-protection grade
Back panel IP 20
45 mm depth--installation
The colour of general input device, meet all kinds of application ROFINET or PROFIBUS DP environment, especially the food and beverage industry.
-5, 7 inches STN display screen
--256 color color
-2 MB user memory
-strong plastic shell using stainless steel front
-streamlined the optimization framework design
-the grooves and minimize joints, the crushed material
-protection grade
The front panel IP 66 K, NEMA 4 x, NEMA 12
Back panel IP 20
http://www.njytouch.com/ContactUs.htm
Infrared Touch Panel
How it works
Infrared technology uses infrared emitter-collector pairs to project an invisible grid of light a small distance over the surface of the screen. When a user touch the surface of screen, the infrared emitted from LED beam is broken ,the absence of the signal at the collector is detected and receiver transmits X-Y axis information to the PC port via touch controller.
Infrared technology is the survivor of harsh applications. It's the only technology that does not rely on an overlay or substrate to register a touch, so it's impossible to physically "wear out" the touch screen. It's an excellent choice for harsh industrial and outdoor kiosk applications.
Model List
Model No. Spec. External Dimension Active Dimension Detail Spec
NJY-0650-IR-N 6.5" 198.40mm x 138.40mm 129.60mm x 97.80mm More
NJY-0840-IR-N 8.4" 230.00mm x 162.00mm 172.00mm x 129.00mm More
NJY-1040-IR-N 10.4" 280.00mm x 210.50mm 210.50mm x 158.50mm More
NJY-1210-IR-N 12.1" 327.20mm x 237.20mm 246.00mm x 185.00mm More
NJY-1400-IR-N 14" 374.00mm x 266.50mm 285.70mm x 214.70mm More
NJY-1500-IR-N 15" 395.00mm x 283.20mm 307.00mm x 231.00mm More
NJY-1700-IR-N 17" 429.20mm x 331.20mm 346.90mm x 261.00mm More
NJY-1700-IR-B 17" 429.20mm x 331.20mm 338.50mm x 271.00mm More
NJY-1900-IR-N 19" 461.00mm x 353.00mm 376.80mm x 302.00mm More
NJY-2100-IR-N 21" 518.00mm x 378.00mm 433.00mm x 325.00mm More
NJY-2300-IR-B 23" 680.00mm x 443.00mm 570.00mm x 344.00mm More
NJY-2600-IR-B 26" 680.00mm x 443.00mm 570.00mm x 344.00mm More
Highlight & Benefits
.Built-in touch systems, aluminum alloy frame,tender apperance,hardly effect the apperance of displays.
.No weakening the illumination of display screen,not indistinct
.High touch precision at 4096 X 4096
.Use any entity of diameter over 8mm
.No delay,fast response
.perate on the screen surface
.operate with finger or stylus/gloved hand
.touch to operate all application software
.manually write, draw, filling up and so on
.operate under -41℃~71℃
.humidity <80% .reliable and stable
.easy mounting, only use RS-232 or USB connection
.highly stable, no drift .durable
.fully sealing,free maintenance
Typical Application
.Gaming machine
.Indoor and outdoor kiosks
.ATMs
.Industrial control
.Pos
.In-vehicle and transportation
.Medical equipment
.Voting machine
I have a machine running on Simatic touch panel Hmi...The Panel failed few days ago..It will take between 5-6 days before the new one arrives.I...
2,379
Hi, We have a simatic Touch Panel OP 177B which is fault. For past 6 months we have been using a mouse to start the conveyors not a fingure...
2,292
Dear all, I was uploaded program from TP177A (Touch panel Simatic TP170 series), i just get PSB file right? So, can i modify it? I want to see...
2,921
Hello Can I download my Protool project from the PG to the touch panels through Ethernet module (CP343-1) then CPU module and MPI. The transfer...
4,366
Hello Can I download my software from the PG to the touch panels through Ethernet module (CP343-1) then CPU module and MPI. The transfer route is...
35
14,305