trouble setting up net-eni
nerdfactormax
Feb 2008
Adelaide
17
I'm having trouble setting up a Net-ENI to connect to a ML1500
I can load and save eni configuration over RS232
I have the eni configured to 192.168.001.254 subnet 255.255.255.0 (the fault light is no longer flashing)
My IP is 192.168.001.253 subnet 255.255.255.0
I can ping the eni module and get a reply, but I can't save and load eni configurations over ethernet (using com port redirector), nor can I see the PLC on RSLinx using ethernet.
Is there anything else I need to setup?
Using RSLinks, how should I be connecting to the plc, linx gateway or ethernet/IP?
Regards,
Colin
In RSLinx I would suggest using the "Ethernet devices" driver. After you create the driver you have to configure it with the IPs of your PLCs and/or NET-ENIs. The Ethernet/IP driver does work but it's kind of flaky so I don't use it.
Also, make sure that the COM port settings (baud rate, etc) of the ENI exactly match those of the PLC it is connected to, or they won't talk.
Hello, We are having trouble setting up a generic ethernet module for a Yaskawa GA80U4168 drive in RSLogix 5000 Version 20.01. All of the...
611
Hello Everyone, I have installed a IC200UEM001 Ethernet Module on my VersaMax PLC. I can set the Temporary IP Address using PME 9.0. The issue...
3,870
Hello all, I'm a student in an advanced level PLC programming class. A project that I'm working on moves boxes through a sorting station and onto...
2,586
Hello all, I recently picked up a MOXA Nport Express DE-311 so that I could try putting a SLC 5/04 on an ethernet network. Apparently what I am...
46
23,928
4,958
Guest
G