WinCC Flex RT and OPC server on the same PC
silviu_r
Dec 2008
Bucharest
Hello,
I have a question regarding an application that I have to make in the near future.
I have 12 intelligent slaves (VIPA 214DP) that will communicate with one Siemens CPU 315PN/DP over Profibus.
I have a PC HMI with WinCC Flexible RT that will comunicate with CPU315PN/DP over Ethernet.
Until this point all is clear.
The problem that I have is the next one: I have to install an OPC server to send information to another system that centralize all the alarms from this building, including my system(refrigeration plant). I want to install the WinCC Flex RT and the OPC server on the same PC. Is this posible? If it is possible what OPC server sollution do you propose?
I hope you can help me,
Silviu
Hi
WinCC flexible runtime has its own OPC server, that can be installed with the runtime engine.
In your wincc project under "Device Settings" select Function as OPC server, If you want the runtime to function as the OPC server.
Stop !
The OPC Server for WinCC Flex only grants access to the tags that have been configured in the WinCC Flex project. Only select this option if you want to limit the access to the target PLC for some reason.
To the original question:
You can install both WinCC Flex RT and the OPC Server on the same PC.
The OPC Server can be Siemens Simatic Softnet IE LEAN, and it can be a 3rd party such as KepWare or Deltalogic.
In case of Siemens Softnet IE Lean, both WinCC Flex PC RT and the OPC Server can be integrated into one and same "PC Station". This has some additional advantages.
i have on the field ML1200 connected thorough serial port to audiotel mc39i gprs modem. i would like to transfer existing connection which goes...
2,006
Hi Guys, Hope someone can help with this one. I have a pc running wincc flex RT. In simatic manager this was originally configured as an HMI...
2,248
Hi, I have a WinCC flexible application with option Act as OPC server active and I cannot reach the OPC server remote. Local is working. When I...
3,570
This is a warning. I am currently investigating if there is a problem or not, but it may take until monday for me to get it confirmed or denied...
3,273
Hi, I'm still doubting about wich way to choose... hmzz There will be a machine, with ethernet connection to an Office PC. They want to be...
57
18,170