Unread November 19th, 2019, 11:06 AM   #1
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 81
1734-AENTR Input light issue

Gaurdlogix 5380 tied into 1734-AENTR. Safety scanner ossd1 and ossd2 are in I0 and I1 respectively. Common is hooked to 4&5. When we reset the scanner we get 24vdc from the scanner at the terminals of I0 and I1. But niether input shows to light up nor swap states in the program. Kinda stuck on this one. i may try to swap in a new input module and see if it works.
  Reply With Quote
Unread November 19th, 2019, 11:49 AM   #2
Geospark
Lifetime Supporting Member
Ireland

Geospark is offline
 
Geospark's Avatar
 
Join Date: Feb 2012
Location: Kildare
Posts: 2,793
You probably need to set the "Point Mode" for the input points in the software?
Without this set the inputs will be inactive.

Go the the module properties for the 1734-IB8S and then to the "Input configuration" tab.

Under "Point Mode", select the Safety function for the individual input points.

Usually for a light curtain or similar you will select "Safety".

You also setup for Single or Dual function here with "Point Operation".

Regards,
George
__________________
"A little nonsense now and then is relished by the wisest men".
  Reply With Quote
Unread November 19th, 2019, 12:16 PM   #3
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 81
Quote:
Originally Posted by Geospark View Post
You probably need to set the "Point Mode" for the input points in the software?
Without this set the inputs will be inactive.

Go the the module properties for the 1734-IB8S and then to the "Input configuration" tab.

Under "Point Mode", select the Safety function for the individual input points.

Usually for a light curtain or similar you will select "Safety".

You also setup for Single or Dual function here with "Point Operation".

Regards,
George
I found it. Just as I read you reply a little bit ago. When our engineer set up this stuff under config he forgot to set the status of the inputs they were set as NOT USED. Not sure why I didnt check that. Could because he said it's good to go haha. Thanks Geospark
  Reply With Quote
Unread November 19th, 2019, 12:22 PM   #4
Ken Roach
Lifetime Supporting Member + Moderator
United States

Ken Roach is offline
 
Ken Roach's Avatar
 
Join Date: Apr 2002
Location: Seattle, WA
Posts: 14,993
The Input channel LED will also remain OFF if the module isn't configured yet, or if it's configured incorrectly for the inputs.

Did you inadvertently associate either of the Test Output signal sources with the inputs ? The inputs would be expecting to see the pulse train from the Test Output, not a steady 24V signal (which would indicate a short to 24V).

Otherwise your wiring sounds correct for a light curtain or safety scanner connection, like the example on Page 62 of the POINT Guard I/O User Manual.

edit: answered correctly while I was looking at the user manual and contemplating coffee.
  Reply With Quote
Unread November 19th, 2019, 01:24 PM   #5
Leukic
Member
United States

Leukic is offline
 
Join Date: Oct 2018
Location: Leesville
Posts: 81
Quote:
Originally Posted by Ken Roach View Post
The Input channel LED will also remain OFF if the module isn't configured yet, or if it's configured incorrectly for the inputs.

Did you inadvertently associate either of the Test Output signal sources with the inputs ? The inputs would be expecting to see the pulse train from the Test Output, not a steady 24V signal (which would indicate a short to 24V).

Otherwise your wiring sounds correct for a light curtain or safety scanner connection, like the example on Page 62 of the POINT Guard I/O User Manual.

edit: answered correctly while I was looking at the user manual and contemplating coffee.
Thanks Ken!
  Reply With Quote
Reply
Jump to Live PLC Question and Answer Forum

Bookmarks


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump

Similar Topics
Thread Thread Starter Forum Replies Last Post
Analog Input 1734 Ie2v flashing red bornwild LIVE PLC Questions And Answers 2 October 26th, 2019 12:41 AM
RSLogix 500 - I/O mapping question toads LIVE PLC Questions And Answers 8 September 25th, 2019 12:40 PM
FactoryTalk View SE Numeric Input Focus zacslade LIVE PLC Questions And Answers 1 March 2nd, 2016 06:26 AM
1762-IF2OF2 Analog Input Problem davidgay LIVE PLC Questions And Answers 22 August 14th, 2013 05:25 AM
Bit shifting? tlvaun LIVE PLC Questions And Answers 17 December 5th, 2002 11:51 PM


All times are GMT -5. The time now is 05:00 AM.


.