I currently have a 1734-AENTR module connected to a PLC in a DLR. When trying to run the program, and going to the AENTR, I run into error code "Code 16#0010 Mode or state of module does not allow object to perform requested service". I do not have any IO modules connected to the AENTR and set the chassis size to 2 as I read elsewhere that the size should be set to the number of modules + 1. No issues with IP configuration. Just wondering if anyone has suggestions on how to resolve this.
Thanks!
Welcome to the PLCTalk forum community !
If you have no I/O modules connected to the 1734-AENTR, then you can set the Chassis Size = 1, or Inhibit the connection, and you won't get any nuisance errors in the I/O tree.
jchadwickB said:
...number of modules + 1...
What you're probably getting confused is that the AENTR itself does not count as a module, but does count toward the chassis size. Hence the requirement to set the chassis size to "number of modules plus one" - you need one "slot" for each of your modules, and one for the adaptor itself.
As Ken says above, set your chassis size to 1 in both the project and the AENTR itself, and the errors should clear.
Although of course, an AENTR with no modules connected to it isn't a whole lot of use to anybody - presumably you're just trying to get things talking and error-free before adding modules?
Hi: I have been using this module for years for my testing. Now it does not work and have no idea how to fix this. Will be very grateful for your...
10,878
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
352
Hello all. I have a remote that uses a 1734-AENTR series C. We had to change it to a new one and, after adjusting the IP and number of slots...
540
The issue we have is that the IT2I thermocouple card and the RTD temperature sensor card connected through a point IO AENTR is constantly trying...
533
Hi guys, I have just recently purchased a 1734-AENTR module so that I could learn how to configure it through LogixDesigner and establish comms...
312