altivar drive
seee
Dec 2010
singapor
112
hello dear friends,
i am going to run a motor with altivar312 in 60hz.
when i give 20ma to it, it run at 50hz even if i
have set the parameter "hsp" to 60hz.
(I mean that motor speed it limited to 50hz.)
please help me.
best regards.
check to see if there is a parameter for min and max. some drives I have worked with looks at the minimum speed ref instead of the max.
thanks for your reply.
As i know only "hsp" parameter is important for change maximum speed.
i have set "hsp" to 60 but maximum motor speed is 50hz.
please help me dear experts.
i am waiting for your help.
Thanks.
If the HSP goes up to 60hz that means TFR is set to 60hz.
In the IO menu what is the AI3 High and Low set to?
Also have you actually measured the milli amps to confirm the drive is receiving 20mA.
Have a look in the SUP menu what the actual reference is the drive is receiving. I believe it is FLR
The only settings that can modify the reference is preset speeds, summing inputs and pi regulator. If you are sure you are giving 20mA then i would just factory reset the drive and choose reference 1 (FR1) again to ai3 and change HSP again to 60 and test. Obviously also enter the motor values again and autotune
Hi Can anyone help please ?? I have a Schneider Altivar 71 that I am replacing with a different drive. It has two terminals bridged LI1 and LI2...
985
Hey everyone. Hope you all are enjoying the new year. I have a pair of Altivar 21 HVAC drives, and I suspect a bad analog input on one of them...
1,454
Good Evening , One more question about the Altivar 320 3 Hp . I would like to use the drive’s 24 vdc power supply to energize a 24 vdc...
1,381
Good Evening , I never set up a Altivar 320 Frequency Drive . I must say I never seen a more complicated drive to set up , LOL How do...
2,097
Hi all, I am trying to control and/or read values from Schneider Altivar12 VFDs. Via Modbus on a AB Micro850 PLC (using the Connected Components...
4,035
