Diagnostics Large Oven
jwyatt8171
Dec 2010
NC
Hey Guys,
I have several thermoforming ovens I am working on. These ovens have 24 heating zones. Each zone may be from 2 heaters in series, to 20 heaters in series parallel configuration. These are what we call cal rods, resistive heaters. 480V system where one zone has 2 SSRs, and L2 doesnt go through an SSR, but is connected (I can upload examples of the wiring if needed.
i have been tasked with setting up diagnostics through the HMI. I am having trouble getting started on this. Space is limited, and I would rather not install new SSRs.
My first through is to use CT(current transformer) connected to analog inputs to the PLC. Can a CT output be connected to a 0-20ma input? I have found some compact CTs that are rated 0-100A with 26ma max output. the highest fuse rating on a zone at the moment is 40amps.
My theory is to have a base amps the zone pulls, and if its out of tolerance we can show a warning for the operator to act on.
Thanks for any input.
Jerry
So, the thought just hit me. Im measuring AC, and the CT output will be AC, not DC current for my PLC input.....Any suggestions?
I have seen CTs with built-in transducers that convert the current to a 4-20 ma signal and I have also seen standalone transducers that take the standard 0-5 amps and convert it to a 4-20 ma signal. I just can't remember any makes for either right now.
Dear Friends, I have few Profinet slaves connected to S7-1200 over Profinet. I wish get alarms and disagnostics from the devices. (IO-Link...
165
Hi all, I heard some cool things today regarding network switch diagnostics (i had usually always brushed over these without much thought.) I was...
169
Hi All, I am taking a deep dive into my facilities HMI Thin Manager Server which has been alarming for High CPU usage. We are using FactoryTalk...
130
Hi, I am using TIA Portal V18. I have imported a (v5.7) SIMATIC manager project via device proxy. I have created a HMI project (TP700) in TIA...
328
We have a project where we have the 1756-L82Es in redundancy with Remote IO Backplant via EN2TRs. Everything works and is redundant but we can...
379