For Ethercat field IO-modules, like f.i. EP2308-0001 from Bechkhoff,
you always have an Ethercat in connection and an Ethercat out connection, to daisy chain the modules.
Is this some kind of 'Ethercat switch', or a strictly electrical connection?
Or in other words, if the fielbus IO module has no power, will the Ethercat be able to pass through to components behind the powerd down module?
What you are saying is correct. EtherCAT IO have a built-in EtherCAT Slave Controller (ESC) chip or ESC supporting SoC (system-on-chip) which controls the forwarding of the EtherCAT packet from one port to the other. As you point out, if one particular node looses power, the nodes to the other side of the master become inaccessible.
That is why most EtherCAT masters support ring redundancy.
I have an Omron NX PLC NX1p2 which Supports EtherCAT . also I have Balluff BNI00HA Ecat Block(IOlink Master). I have setup communications and...
175
If an IPC with Codesys runtime on it has two separate ethernet ports, is it possible to have an Ethercat master on each of them? I do not find...
552
Hello everybody. I encountered a problem - I don’t know how to update the firmware on the Mitsu MR-J5-40G-N1 (ethercat) servo amplifier. My...
422
Just curious if anyone has been down this road before? Considered using one of the anybus gateway adapters, experience with them. Master...
684
Afternoon all, So, i have an output that is being fired from 2 inputs separately. 1st input is a sensor, when something passes by it should...
332