Hi
We had a faulty DO card giving SF error in our Siemens PLC setup model 326-2BF01-0AB0 and we replaced this 326-2BF41-0AB0 I/O card.
We updated the hardware configuration for the new module, set the correct DIP switch settings as per the new Address assigned by the system
After downloading, the SF error is no longer there and everything is good on the card.
But whenever we try to Force any of the output channel from the force table, the card goes to fault and then we have to reset the card again the card and the error goes away and the card becomes healthy.
Any help on this will be highly appreciated
The 326-2BF41-0AB0 looks to be a failsafe module. You can't force failsafe I/O.
What are you trying to accomplish with the forcing?.
Hi, I didn't know we can't force the fail safe modules by forcing the I/o we are trying to see if the comected I/O points are working or not that is why we tried forcing the I/o from the variable table.
Be sure to revalidate the safety functions related to that card and perform the acceptance test. This is required to comply with safety standards.
How to revalidate the safety functions related to that card?
Hello RVaughan
Can you please help me on how to revalidate the safety functions related to that card and perform the acceptance test?
Will appreciate any help on this?
146
Hello all. I have an ESA HMI that is connected to a Simatic S7-300 (CPU312). I have uploaded the program from the PLC which is written with Step7...
1,500
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
735
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
1,090
G'day guys, I am setting up a s7-300 as a test rig for the workshop and when I downloaded the PLC is not going into run mode, I keep getting a...
35
5,375