Aentr problem
buoanventura
Jun 2011
italy
Hi, I have problem with Aentr and compact logix sistem:
1769-L32E ethernet
1734-AENTR Adapter
Set ip adress with Bootp_dhcp.
I see the aentr on linx, ping is ok but on I/O configuration the module has error (connection time out). All the led (aentr) are green only the network status flash green every 20-30 sec.
I try to reset the module but the problem persist
What revision is all your hardware at? I just started researching installing one of these and the 6th page of the manual outlines what revisions are necessary.
If using the adapter with a 1756-ENBT module, 1768-ENBT module or an L3xE processor, use the following required firmware versions for these bridge modules:
If you use the BootP utility to assign IP addresses to the adapter, use version 2.3.2 or greater. • 1756-ENBT firmware version 4.5 or greater • 1768-ENBT firmware version 2.1 or greater • L3xE processor firmware version 17 or greater
http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1738-in028_-en-e.pdf
I'm looking to see if I can use one of these to connect a Micrologix 1400 to Controllogix5000 so please post up how your install has gone.
We had recently upgraded Rockwell control system from ControlNet to Ethernet (1719-AENTR). and in last couple of months 2 different AENTR devices...
181
Hello The plant is running and there is no shutdown nowadays therefore I can add 1734- AENTR and its card while PLC is in Run? I do not wanna...
348
Hello all. I have a remote that uses a 1734-AENTR series C. We had to change it to a new one and, after adjusting the IP and number of slots...
536
The issue we have is that the IT2I thermocouple card and the RTD temperature sensor card connected through a point IO AENTR is constantly trying...
530
Hi guys, I have just recently purchased a 1734-AENTR module so that I could learn how to configure it through LogixDesigner and establish comms...
309