You are going to need some information about the lighting circuits. How many fixtures are on each electrical circuit? That depends on the watts and volts of the fixtures. Generally you can assume 8 to 10 fixtures per circuit. If each side has 8 circuits, then you need 8 on/off digitial outputs for each side, or 32 total. You could use a Remote I/O module in the center of each side, with a local light fixture power supply and RIO power supply for each, and a Ethernet cable (one cable can loop to and control ALL RIO modules) from each (or another PLC communications protocol) going back to a main control PLC and control HMI. You may even need transformers at the location of each RIO module to reduce a higher main voltage down to the fixture voltage.
For these long distances, you probably will want to keep the light fixture voltage as high as possible, maybe 480, 380, or 277 volts. This will reduce the current on each circuit (that your Remote I/O modules have to switch on and off).
If verification feedback is required for each circuit (or each fixture), then you also need some current-monitoring sensors that provide "Burning/Not Burning" inputs to Input terminals on your RIO modules. You can probably monitor the current on each fixture supply circuit, and use that to determine if any of the fixtures on that circuit are not ON. The currrent levels should be fixed for each numuber of fixtures that are actually drawing power on each circuit. For example, if you are using 400 watt metal halide lamps (which draw about 460 to 480 watts) at 480 volts, the current for one fixture should be about 1 amp. If there are 8 fixtures on the circuit, then the total for that circuit should be about 8 amps. If it is only 7 amps, then probably 1 fixture is not burning. Your PLC monitoring program would have to take into account the starting time for the fixture, depending on what type of fixture you use, to make sure that you are looking at the running currents and not the start-up currents.
Another montioring method would be to use photoswitches at each fixture, but that would require much more wiring and installation costs. Each fixture would have an input back to your RIO modules, where the current monitors only need 1 input per fixuture circuit (which can be located at the RIO panel so that field wiring is minimized).